Wiring heating element

Tue Jan 19, 2010 5:50 pm

I am trying to figure out the wiring for a 110 volt 1400 watt water heater element. I tried running a 20 amp switch in line with the two black wires to one side of the switch, ground to the other side, and two white wires nutted together in switch box. Then black wire and white wire go from the switch to the two screw terminals on the element and the ground attaches to a small bolt that I welded onto the stainless plate that the element is threaded into. When I try to turn on the switch to test it, the breaker trips immediately. I did use teflon tape when I screwed the element into the plate, could this be breaking continuity from where the ground wire attaches and the element threads? Any ideas are appreciated. Thanks
slick
 
Posts: 27
Joined: Tue Sep 29, 2009 5:45 pm

Re: Wiring heating element

Tue Jan 19, 2010 7:39 pm

If I'm reading this right you wired hot (black) to one side of the switch and ground to the other. When you close the switch you are connecting hot to ground which is tied to neutral at the panel and it shouldn't be much of a surprise that the breaker trips.

The right way to do this is to wire hot (black) from the feed to one side of the switch and then run another black wire to the hot side of the heater. White (neutral) from the feed goes to the other side of the heater (can be connected to the white wire from the feed). Earth (ground - bare, green or green with yellow tracer) should be connected only to the earth connection on the heater and the earth connection on the switch if it has one.

I would strongly advise consulting an electrician.
ajdelange
 
Posts: 1386
Joined: Wed May 27, 2009 9:18 am

Re: Wiring heating element

Tue Jan 19, 2010 9:05 pm

Switches are just devices that interrupt and connect the Hot OR Ground sides of the Load/Power-Supply, they are not meant to be a load :)
Conical Fermenter - Amber Lager
Keg#1 Dunkel
Keg#2 Helles
Keg#3 Flanders Red
Keg#4 Star San
Keg#5 Star San
Keg#6 Star San
User avatar
Kbar
 
Posts: 984
Joined: Tue Nov 11, 2008 4:43 pm
Location: Portland, Oregon

Re: Wiring heating element

Wed Jan 20, 2010 5:01 am

Kbar wrote:Switches are just devices that interrupt and connect the Hot OR Ground sides of the Load/Power-Supply


While it is true that one can interrupt a circuit anywhere within it, it is bad advice indeed to suggest controlling a circuit by switching its neutral and I'm certain it violates the code. The reason is obvious: while current cannot return through the neutral while the switch is open it can return through you should you touch any part of the circuit including the neutral side of the load or the load side of the switch. Also an accidental connection between the neutral side of the load and ground would energize the load even though the switch open. With the correct wiring such a fault would have no detrimental effect. While a GFCI (ELCB) would protect you against either of these eventualities this is not what what they are really for. You can certainly use a DPST switch to open the neutral AND the phase thus completely isolating the load from the feed but putting the switch in the neutral is a no-no.
ajdelange
 
Posts: 1386
Joined: Wed May 27, 2009 9:18 am

Re: Wiring heating element

Wed Jan 20, 2010 7:57 am

ajdelange wrote:
Kbar wrote:Switches are just devices that interrupt and connect the Hot OR Ground sides of the Load/Power-Supply


While it is true that one can interrupt a circuit anywhere within it, it is bad advice indeed to suggest controlling a circuit by switching its neutral and I'm certain it violates the code. The reason is obvious: while current cannot return through the neutral while the switch is open it can return through you should you touch any part of the circuit including the neutral side of the load or the load side of the switch. Also an accidental connection between the neutral side of the load and ground would energize the load even though the switch open. With the correct wiring such a fault would have no detrimental effect. While a GFCI (ELCB) would protect you against either of these eventualities this is not what what they are really for. You can certainly use a DPST switch to open the neutral AND the phase thus completely isolating the load from the feed but putting the switch in the neutral is a no-no.


Good Point. We sometimes do this in off road machinery, but those are 12-24V DC systems, on coils and other feedback devices. Household wiriing should be on the hot side. Good stuff!
Conical Fermenter - Amber Lager
Keg#1 Dunkel
Keg#2 Helles
Keg#3 Flanders Red
Keg#4 Star San
Keg#5 Star San
Keg#6 Star San
User avatar
Kbar
 
Posts: 984
Joined: Tue Nov 11, 2008 4:43 pm
Location: Portland, Oregon

Re: Wiring heating element

Thu Jan 21, 2010 4:17 am

Thanks to all who replied. I finally got out my tester and discovered that AJ was right in his post. I was not familiar with this heavy duty switch as the connections are a bit different that the standard household type. Anyway, what I have is the element that is housed by a 10 inch section of 2 1/2 inch stainless pipe with triclover caps on each end, the element is threaded into one of them. There is an inlet on one end of the pipe and an outlet on top for circulation of wort. What I am wondering now is, what is the best way to control it? Do I need a relay? and where is the best place to locate the probe for the controller(I know this could incite an argument) Also maybe a good source for these items. Thanks again to all. slick
slick
 
Posts: 27
Joined: Tue Sep 29, 2009 5:45 pm

Re: Wiring heating element

Thu Jan 21, 2010 5:45 am

There are lots of options for control. The simplest is to wire a diode in series with the element and put a switch across it. With the line switch off, the element is off. With the line switch on and the diode switch off (open) the heater is at half power and with both switches closed it is at full power.

Another approach is a Variac - a manually adjustable autotransformer which allows control of the power anywhere from 0 to about 110% of full.

As you mention a probe I assume you want automatic control which means an automatic controller. There are several types of these. The simplest (differential type) closes a switch when the temperature gets below a set point and then opens when it rises a certain number of degrees (that you can usually adjust) above that. These are fine for freezers and fermenters (where the action is reversed relative to the way I described it) but can't control any better than the width of the differential (deadband).

The most capable and generic controllers are of the PID (Proportional, Integral, Differential) variety and the more modern fuzzy logic ones. They hold temperature and respond to changes in set point and load rapidly without overshoot if tuned properly. Most controllers today are equipped with an autotune feature which is a plus in the sense that you don't have to know how to tune a controller and bad news in the sense that the autotune features don't always give the best "tune set" but you can usually arrive at a good tune set by tweaking the one the device comes up with. Setting up a PID controller is a bit of an art.

Another variable with PID control is the form of the output. This can be a continuous signal from 0 - 100% (either a 0 - 5 Vdc voltage or 4 - 20 ma current) going to a solid state device which controls the firing of SCRs (for 10% power they conduct for 1 half cycle out of 10, for 50% on every other half cycle etc.) These setups are expensive but with all the stuff on e-bay you might pick one up at reasonable cost. For the typical brewing application on-off (proportional) control should be OK. Here if the controller wants 10% power it sets a control signal (usually TTL logic level i.e. 5 VDC but the output may be just a pair of relay contacts) high for 10% of a cycle time e.g. 3 out of 30 seconds. For 20 percent it is high 6 seconds and off for 24 and so on. The control signal operates a relay (solid state is fine and they don't have contacts which can weld) and you will definitely need this unless your controller is equipped with a relay with contacts hefty enough to carry the load which is unlikely. Note that the continuous system is effectively the same except that the basic unit of condution is the 8.33 ms of a half cycle of the line. As a final note: most modern PID controllers will have a differential mode as well.

Then there is the matter of the sensor. First as to the placement - the sensor should be located at the point at which you want to control the temperature. At the outlet of the heater tube may seem an obvious choice but for time proportional control I would expect problems unless the flow rate is so fast that the rise through the heater tube is very small. A more sensible placement would seem to be where the flow enters the heater tube - similar to the concept of installing a house thermostat close to the air return duct inlet. Another possibility would be where the fluid leaves the reservoir (mash tun, I assume) or elsewhere in the reservoir itself.

Still on probe there is the question of the type. Most controllers accept RTD, thermister and thermocouple input. For brewing RTD's are, IMO, the most practical though certainly the other types can be made to serve.

As to where to get this stuff: sources abound. Cole Parmer, Omega Engineering, Watlow, Eurotherm, Cal..... As you probably don't want to be shelling out for new Ebay seems a good place to search. The problem you will face is a surfeit of choices. As this is obviously a fairly complex area I'd suggest imitating someone else's success. Give the readers additional detail on what you are trying to do. Someone on this forum probably has a similar system and may be able to suggest sources for components.