Thermowell placement is very dependant on type of system.
On a gas fired mash tun, a thermowell at the exit works well because your pulling your liquid just past your heating device. This same type of placement on a system with a heat exchanger caused me all kinds of grief, here is why.
Let's say I set up everything to mash at 152, got my pump started recirculating and my mash is cruising at 152. When the output of the mash tun drops to 151, the love control signals for more heat and turns on the heat exchanger. The heat exchanger I use can get about a 20 degree differential with recirculation. so if I'm at 151, it heats the wort to about 171 and it is then pumped on top of the mash. By the time the wort heated to 171 gets to the output to signal that enough heat has been applied, the body of the mash has had so much heat added that it continues to climb even with the heat off. In my case it stopped climbing at 168 but that was after adding some ice and opening the lid. Kind of ruined that beer.
I now use a thermowell at the output of the heat exchanger. This works great for single temp mash's. I still monitor the output of the mash like a brutus just to see how I do and it is usually within 1 degree of my set temp. For a step mash, I will adjust the love up to about 170 for 10 minutes which begins to raise the temp of the mash with 170 degree wort, but I end up adding some boiling water to help.